DIY Alternative zu Nibe Modbus Modul
The affected messages were always 81 bytes long and included 5c5c. I found the problem yesterday. Line 107 in backend.js let index = data.findIndex(index => index == 92); if(index!=-1) { data = data.slice(index, data.length); fs_start = true; } I should have blocked this with if(fs_start===false)... If a new 5C is found then it will slice all the data before that and then concat the buffers. Thats why I'm getting shorts. I rebuilded the backend to handle the buffer directly (instead of converting it to array) And added the if(fs_start===false). Now I have 0 errors during the last 18 hours. I believe the problems of NibePi are solved :D I'm gonna run some more testing but it looks really promising now. Could'nt have done this without your help JanRi and the others who contributed. Now NibePi handles all the communication with the pump directly and holds all the registers for every pump in the F series and automatically discovers them. When all the communication troubles now hopefully are solved I can move on to make the NodeRED nodes complete. |
Hi, Great! That's how it should be. Yes, thats looks good. The remaining question then is what happens in case of higher CPU load. If this leads to only one missed ACK from time to time I guess it will not raise an alarm. I have not yet figured out how many missed ACKs are still okay but appr. one second with no ACK seems to be no problem (stop nibegw, compile, start). Btw... in my 100000 logged messages so far there was no double 5c5c, i.e., message length 82 (or 8 in case of type 106). Theoretically, this should be possible but very rare. Greetings, Jan |
I have done some CPU stress testing and I see no errors. Yes I agree, NibePi should handle them well since it loops through the whole buffer. |
Hi, I got something very strange... my client side alarmcounter increased to 1 at night. It gets always increased if the previous value of register 45001 (part of favorites) was 0 and the current value != 0 (if it is 0xfb then error is reset - this is modbus error). However, there was no alarm at the heat pump, no alarm or info message in uplink, no error output from nibegw and, most curious, no message in the UDP log that contained a 45001 value that differed from zero. I have to investigate that further but I'm afraid that was just some strange "glitch" at node.js side (running on server with ECC memory, so even this is out). If there are findings that are of interest beyond by setup, I will tell it here. What type of stress test? I recommend running a multi threaded load that consumes a lot of CPU time as a worst case scenario to figure out the limits are. Example: openssl speed -multi X It needs some time to finish so its a good test. X is the number of threads. On your single core, I would go up to 8 or 10 or until problems occur. I'm quite sure that there will be problems once the load becomes too high but this would also apply to nibegw if run on a core that it shares with others. So the goal should be to figure out how much load leads to some problems but no alarms and how much load leads to alarms. This is especially interesting to see how much workload can be put on the NodeReds in case of a single core Pi. If it runs perfectly with X=3...4 I would not expect problems for the purpose of NibePi. And, if there will be one error per month or so, this does not matter. Greetings, Jan |
This test. https://core-electronics.com.au/tutorials/stress-testing-your-raspberry-pi.html Probably not an accurate test, there were no issues, then I tested with creating an endless loop from NodeRED to my worker (index.js), I let it run for a couple of minutes and there no errors, even when the load was in my worker. Now I'm running your test, seems like a good choice! How long does it run? |
Hi, This put maximal thermal stress at the cpu. However, it does that with just one thread per core so at the useal 100...1000 Hz scheduler frequency that should be no problem. In our case, we do not want to stress the hardware but the os scheduler with many fully loaded threads. Basically, this is the speed test of openssl testing several crypto algorithms. It depends on CPU speed but it might run for several hours on a Pi. This is not necessary here! I would test this for each number of threads (so X=1...10) for appr. three to five minutes (Ctrl-C stops it). If there is a problem with scheduling, it will occur in this time. In order to save time, start with X=10. If this runs perfect for 5 minutes, smaller X (less threads) will also run (so there is no need to test that). If not, redude X until it runs stable. I have not tested this for nibegw as my quad core Pi easily can reserve one core for nibegw - in this case the load on the other cores (more or less) does not matter. Obviously, this solution does not work on a single core Pi Zero. openssl speed does not stress the IO subsystem but this is no issue here as you do not plan to stress that. Your SD is read-only so writing large amounts of data is out of scope and beside MQTT and some HTTP you do not do heavy network IO. Greetings, Jan |
I am done testing. The test completes at 15 threads. Anything above the whole raspberry crashes. During the test there are no errors and the modbus alarm never comes. It was s good test and I'm very happy with the results. Im also gonna try nibegw at 15 threads. |
@janri What about the preemptive real time Kernel Patches (Preempt-RT)? I guess they could bei useful to make the system more robust agsinst too high latencies caused by high system load. |
The test with 15 threads was also succeded with nibegw. I dont believe there are any timing issues running nibegw or nibepi on a raspberry pi which is being used for other causes. |
Hi, although I'm still think that there is the remote possibility of timing issues, I agree that this will not affect operation. Even if you miss two or three ACKs, this will not lead to an alarm (you stop and restart nibegw without alarm, even recompile inbetween). Our usual 80 byte message is 87 byte long. At 9600 baud 8N1 this is 870 bit, appr. 90 ms. This is a lot of time for such a processor, even at high load. I'm pretty sure that we CAN produce problems by writing very large files to very slow USB or SD devices. But thats not our intention so we can ignore that. This is most likely due to the fact that you run out of memory. You do not have swap and the Zero has not that much RAM. I guess that you might come a little bit further with nibegw as this requires less RAM that node.js. It can help but also have issues. As I already told before, we had such a problem at work for a Pi-based demonstrator. Here, load and timing requirements were much, much harder. At the end, we could only make it stable enough (for demonstration purpose, not production use) by putting the controller isolated on one of the four cores of our Pi 3B (so significantly more CPU power than my Pi2 and miles ahead of a Pi Zero) AND had to use the Preempt-RT-patches. Here, the "other load" consisted of a full blown GUI and some other stuff. Greetings, Jan |
Hallo zusammen, ich werde demnächst versuchen meine 1255 mithilfe von SPS Wago 750-8212 aufzuschalten. Hat schon jemand es versucht oder plant so was zukünftig durchzuführen? Ein Programmcode für Standart-Modbus Kommunikation ist vorhanden, muss jetzt für Nibe Protokol angepasst werden. Danach können die Daten von WP WP [Wärmepumpe] weiterleiten bzw. speichern. (Cloud/KNX/Modbus-TCP/FTP/SD-CARD/ LON usw.) |
Nein, eine SPS-Implementierung kenne ich nicht. Ist halt die Frage ob sich der Aufwand überhaupt auszahlt, nachdem andere Lösungen schon mehr oder weniger fertig verfügbar sind. |
Hi, "direkt anschliessen" halte ich für extrem aufwendig. Die Pakete müssen alle einzeln bestätigt werden. Das ganze ist zwar RS485, aber das Protokoll darauf ist ein Nibe-Eigengewächs. Du musst das also komplett von vorne bauen. Mit Modbus hat das nur insofern was zu tun, dass Modbus auch über RS485 geht und es von Nibe für extrem viel Geld das Modbus 40 gibt, das ein Adapter zwischen diesem Protokoll und Modbus ist. Wenn, dann geh den Nibegw + Arduino-Weg. Das spuckt dann UDP-Pakete aus, die du auch ignorieren kannst, ohne dass das zu Problemen führt (was direkt auf dem Nibe-RS485 nicht gilt). Die müsstest du dann auf was auch immer umsetzen, das ist aber ziemlich einfach, wenn man diesen Thread liest und sich die hier gezeigten bzw. diskutierten Codeschnipsel anschaut. Meine Lösung aus NibeGW auf RPI2 und selbstgebauter UDP<->MQTT-Translator (auf Server) und Logging/Anzeigeclient per MQTT läuft seit Anfang der Woche ohne jedes Problem 24/7. Aktuell wird gerade WW WW [Warmwasser] gemacht: AT: 8.5 IT: 21.9 AT_48h: 5.5 VL: 46.7 RL RL [Rücklauf]: 27.5 exVL: 23.1 VLsoll: 23.2 Kond.VL: 46.4 Heissgas: 68.4 Sauggas: 6.9 SoleEin: 4.0 SoleAus: 0.6 BWoben: 44.2 BWunten: 43.8 WQ: 27 % WT: 8 % WT: 4.0 l/min Kompr. 55.0 Hz Relais: 15 Starts: 187 -345.2 GM Spreizung: 19.2 P_th: 5359 W P_ko: 876.2 W P_pu: 28.4 P_el 904.6 AZ: 5.924 EZ Kompressor: 2330.4 KWh EZ Pumpen: 392.7 KWh WMZ Heizung: 13471.3 KWh WMZ WW WW [Warmwasser]: 662.4 KWh WMZ Kuehl: 0.0 KWh Betriebsstunden: 5650 Betriebsstunden WW WW [Warmwasser]: 232 Alarmzaehler: 0 Alarm: 0 Nachrichten: 106534 Die Echtzeit-AZ stimmt bei WW WW [Warmwasser] nicht, weil der Durchflussmesser hier zuviel anzeigt. Real dürften es um 4000W und eine AZ um 4 sein. Viele Grüße, Jan |
Hi, die SPS Implementierung ist sehr ähnlich wie C oder C++ (alles irgendwie von C abgeleitet). Den vorhandenen Code für (Arduno/RPI) schaffe ich schon irgendwann auf ST anzupassen. Ist nur mit Zeitaufwand verbunden. Wago ist schon verbaut und steuert alles im Haus (KNX / Dali/ Modbus Raumbediengeräte), deswegen möchte ich direkt nutzen. Eine weitere SPS für Testen ohne Haus immer dunkel zu machen ist auch vorhanden. )) Ich berichte wenn es geklappt hat. Weinachten habe ich mehr Zeit dafür. Gruß Niko |
Wenn ich es richtig verstanden habe setzt die 1.1 auf node red Von node red aus kannst du problemlos modbus tcp oder auch auf den KNX Bus schreiben und hast auch gleich ein tolles Werkzeug um allerhand iot geraffel anzubinden Vielleicht gibt's auch direkt eine Integration, evtl. hilfreich das Wago für node red sogar einen Kurs anbietet https://www.wago.com/de/events/seminar/iot-mit-e-cockpit-docker-node-red |
Hi, NibePi 1.1 wird auf NodeRed setzen - fertig ist das noch nicht, da baut der Entwickler noch dran. NibePi 1.1 braucht aber zwingend einen RPi, solange niemand ein UDP-Interface einbaut (dann könnte es auch auf irgendeinem Node.js-fähigen Server laufen und seine Daten via nibegw von einem Arduino oder RPi bekommen). Wenn du da was für die Wago bastelst, würde ich über UDP gehen. Das würde dann einen Arduino + Kleinkram für ca. 20 Euro an der WP WP [Wärmepumpe] bedeuten (da läuft dann nibegw) und das bläst die Daten dann per UDP raus. Das wiederum müsstest du dann mit der Wago decodieren. Ich denke nicht, dass das viel schwerer als der Weg über NodeRed ist... aber das kommt dann vor allem auf deine Programmiervorlieben an. Oder du suchst einen Weg, über MQTT auf die Wago zu gehen. Viele Grüße, Jan |
NibePi 1.1 funktioniert unter allen Linux-Betriebssystemen mit RS232-RS485.
Wenn es fertig ist ...
Wago 8202 hätt ich auch zum Spass verbaut für Alarm, KWL, VSR, Heizungs, Pool, Energiemanagement usw Steuerung verbaut. Mit RS485 Klemmen usw... Wenn du was lauffähiges für E.Cockpit hättest, wäre ich interessiert :)... Ansonsten obs aufn Linux BSP auf der SPS lauffähig is, ist fraglich.. wenn nicht Linuxserver oder Nas oder Rpi.. Udp Variante mit Node Red wäre auch interssanr |
Found my old Raspberry B + and a cheap adapter too, but that should work? Maybe you can already say something about the status of V1.1, I'm curious :) |
Hi, It should work after changing the serial port from /dev/ttyAMA0 to /dev/ttyUSB0. There was nothing from the author after the last post but I guess he is busy finishing 1.1. In the meantime, you can try your hardware with the old version or with nibegw and a small UDP server. My code (UDP<->MQTT) is not "production ready", it is more a prove of concept that still has unfinished features, but it runs rock stable since appr. four weeks. Since it gives less functionality than nibepi, I do not plan to publish it (yet) but I can imagine to give it somebody to continue development. Greetings, Jan
Danke gut zu hören, ich bau die Hardware jezt erst mal ein und schau dann weiter |